Folks
Had this setup for the last 2 years and have not had any issues but in the last 6 months noticed the leasure battery was flat in the monring
Setup
2 X TNE12-100 , AGM 100 amsp, two batteries so giving a total of 200 Ah
Fridge CR-0050 Waeco
Solar panel 325 Watt with Victron mmpt 100/30
Simple BM2 battery monitor that only showed %
So recently installed Victron Smart shunt 300 amps
Made sure battries where 100% full from both the Shunt and BM2
Disabled the mmpt so no charge was going to the battries.
Turned the fridge on to Setting 3
Current 4.45A , Power 60W

Then left it until approx 11pm
Noticed the Shunt and BMI where down to 10% ,should not have been anywhere near that
If my run time calculation is correct
Hrs = Battery Capacity Ah X Volatage / Consumption W
40hrs = 200Ah X 12 Volts / 60 Watts
I know AGM should only be distarged to 50% so dived by 2
Gives a run time of approx 20hrs
At this point I tured the fridge off and MPPT on (It is night so dont expect it to charge)
In the morning I checked the shunt graphs

As you can see the voltage is going down as expected , however at approx 9pm it ssems the voltage just drops off a cliff and repidly drops from 12.77V to approx 11V
So not sure if the issue is with the fridge just deciding to consume all the power or if the battery's are the issue.
Is there a better way to test this or anbody has any thoughts , would be very welcome.
Had this setup for the last 2 years and have not had any issues but in the last 6 months noticed the leasure battery was flat in the monring
Setup
2 X TNE12-100 , AGM 100 amsp, two batteries so giving a total of 200 Ah
Fridge CR-0050 Waeco
Solar panel 325 Watt with Victron mmpt 100/30
Simple BM2 battery monitor that only showed %
So recently installed Victron Smart shunt 300 amps
Made sure battries where 100% full from both the Shunt and BM2
Disabled the mmpt so no charge was going to the battries.
Turned the fridge on to Setting 3
Current 4.45A , Power 60W

Then left it until approx 11pm
Noticed the Shunt and BMI where down to 10% ,should not have been anywhere near that
If my run time calculation is correct
Hrs = Battery Capacity Ah X Volatage / Consumption W
40hrs = 200Ah X 12 Volts / 60 Watts
I know AGM should only be distarged to 50% so dived by 2
Gives a run time of approx 20hrs
At this point I tured the fridge off and MPPT on (It is night so dont expect it to charge)
In the morning I checked the shunt graphs

As you can see the voltage is going down as expected , however at approx 9pm it ssems the voltage just drops off a cliff and repidly drops from 12.77V to approx 11V
So not sure if the issue is with the fridge just deciding to consume all the power or if the battery's are the issue.
Is there a better way to test this or anbody has any thoughts , would be very welcome.