I think that happened at one site.
But on another we took out the other 3 and still ours tripped it.
Silly question but we had been travelling so our leisure battery was full.....would this cause a surge on hookup? And trip the EHU?
Most likely you tripped campsite’s residual-current circuit breaker (RCD, RCCB). Within EU all outdoor electric installations must have (=>should have) one. Actually that’s the case only for installations of last 15+ years, earlier ones might lack the protection. The function of a RCD is to monitor that all the current is consumed only by the appliance (the van), and absolutely no current (usually set to trigger at 0.040A) leaks to the earth, either through wet feet or faulty insulation or faulty connection.
The immediate tripping hints there being a connection between neutral (or live!!
) and PE (protective earth, the chassis of van) in your van as you mentioned you being the only one hooked, and no significant loads to trip overload protection. Should be easy to verify.
Just a note: residual-current circuit breakers are not sensitive to load or surge, only thing that matters is the leak current from live/neutral to earth.
- - -
Reverse polarity thing refers pretty much to the times of vacuum tube radios and tv’s. Those things had a chassis inside which was connected normally to neutral, and so being safe even to touch. But if for some reason (for example faulty extension cord!) live and neutral were reversed… You still could find similar setup in old beautiful lamps with metallic structures. They rely on neutral being connected neutral.
Because in many countries in continental Europe you can plug your 230VAC appliances either way (German type of wall socket, which can be used also outdoors), both live and neutral must be/have been electrically isolated from chassis/earth in all appliances sold in EU – so the problem has been solved decades ago. If reversing the polarity would have made any difference; I would be really concerned…