Just as matter of dicussion, what you say is theoretically correct (not saying it is legal in UK) only if you have just ONE derivative circuit limited at 10A . If you had 2 or 3 you could let your loads take 20 or 30 A from your input circuit. That is obviously not safe. In practice, except the most simple cases , you you always need a main max current protection, in your case likely being a 16A breaker.Not saying you don’t need over-current protection on the incoming of course, seems wise to have it too rather than just an RCD. Although given it’s running straight into the MCBs anyway maybe it’s overkill.
Just as matter of dicussion, what you say is theoretically correct (not saying it is legal in UK) only if you have just ONE derivative circuit limited at 10A . If you had 2 or 3 you could let your loads take 20 or 30 A from your input circuit. That is obviously not safe. In practice, except the most simple cases , you you always need a main max current protection, in your case likely being a 16A breaker.
Thanks for the info Stay Frosty, nice to hear from an Electrician.That 63A 30mA RCBO is going to be receiving power from a 16A supply so way oversize for over current protection and never likely to trip before the site power RCBO unless via an earth leakage fault.
When you started the thread with the kit shown you were ok, as often happens offered advice has dragged the subject all over the place and doubt has crept in, I'm waiting for someone to come in and quote the IEE regs for a TT installation complete with earth stake.
Going back to that 63A RCBO you would need a 16mm2 individual conductor size in your extension lead compared to the normal 2.5mm2 so go back to the original items.
Be aware that with a 25A 30mA RCBO on the incomer though there's every likelihood that the site 16A 30mA RCBO will most likely trip in an overcurrent fault ahead of your larger capacity of 25A, I use a 16A 30mA RCBO as the incomer and a 10A single pole MCB for our one twin skt.
I should point out I don't normally use an EHU though and our 230V comes from a 2kW inverter which is a whole other minefield.![]()
I've yet to see a pre populated Campervan Consumer unit with an RCBO, thy all seem to have standard DP RCD. What are the benefits/pros/cons of one over the other then?As @t0mb0 had spotted and I hadn't your 63A 30mA RCD was just that and not an RCBO as I thought so I would swap that out for a 16A 30mA RCBO and stick with your 10A DP mcbs.
It's a ball ache resetting the 16A RCBO every five minutes if it turns out your appliances plugged into those two twin 13A skts are trying to pull 20 odd Amps but they would also knock out the site 16A hookup RCBO too.
Just a case of remembering you've only got about 3.5 kW to play with not four lots of 3kW, as for not using Chinese kit it's pretty much that or Indian from the national DIY places regardless of where the stuff was designed but generally most of it is fit for purpose.
I've yet to see a pre populated Campervan Consumer unit with an RCBO, thy all seem to have standard DP RCD. What are the benefits/pros/cons of one over the other then?
So I'd still need the 2 DP MCBs as well as the RCBO, Correct?The RCD doesn’t limit max current at all, it just protects against current leakage. Therefore, if you have two 10A MCB circuits you could be pulling 20A total. An RCBO is effectively an RCD combined with an MCB.
So I'd still need the 2 DP MCBs as well as the RCBO, Correct?
So, i want it as safe as possible, especially as we will be visiting 5 campsites on the continent all with EHU and I don't want to have to worry about reverse polarity.Yes, it wouldn’t replace the per-circuit MCBs. I’m afraid I don’t know what the actual regulations are though, as you say, plenty of places are selling pre-populated van boxes with RCD plus two MCBs.
Yup.
What I was trying to indicate earlier in the thread is that you're only going to be able to draw 16A worth of electric from the site's 16A blue outlet skt before their RCBO thinks about tripping.
In reality this will depend on the site's protective device but effectively with a 13A outlet equalling 3kW output 16A doesn't add much to the mix with a further just under 700 Watts so 3.7kW @ 230V so however many 230V skts you have in the van 3.7kW is the point where a protective device, yours or the site's will start thinking about dropping out.
Domestic mcbs are type b with c type being more like the old motor rated type which historically tolerated inductive loads like electric motors, transformers and the old school fluorescent lights, disconnection times normally decide the use of type b at home.
They make 2 Pole RCBO's nowadays, look for neutral switching in the bumpf. They are /can be narrow format MCB style as well so reduces the size of consumer unit that is required.So I'd still need the 2 DP MCBs as well as the RCBO, Correct?