Quick question for people who have a Renogy 2000W inverter.
Renogy suggest fitting a 250A fuse (even though they supply 100A cables - another discussion).
At 2000W and 12v is a current of 167A (plus losses for the inverter).
I would be interested in what size cable you used and for what length of run? I am thinking 50mm2 as the run will be less than 0.5m each way.
Thanks.