Any advice from a qualified domestic sparky is much appreciated.
I’m an engineer with plenty of diagnostic experience inc electrical, just not IEEE qualified....!!
My house is served by a very unreliable underground mains cable (Western Power) that has caused loads of power outages over the years, several freezers defrosted while I’ve been away from home.
I noticed about a 6 months ago that my power was tripping more than my neighbours and also when there wasn’t a power outage.
I have two separate parts to the house, each having it’s own consumer unit but fed from the same meter. A couple of months back I located a Neutral to Ground fault and isolated it to one side of the house, after disconnecting the Neutrals one at a time from the consumer unit bus bar I found the faulty circuit. Next I disconnected the affected circuits neutral cables at sockets and junctions until I isolated the individual cable, then I found and fixed the fault. It was a Neutral conductor wire cut on the end of steel conduit.
I have just checked Neutral to Ground again and an insulation fault was back, this time far worse at just 0.5 Ohm, why hasn’t my power tripped I’m thinking.
Again I disconnected Neutrals but this time the the fault didn’t clear and I could not find an insulation fault on the house wiring with my meter.
The fault was only present with the 80A RCD ON so I switched off the RCD and disconnected the consumer unit ground busbar from the supply cable ground. Now I measured from the Neutral meter tail connection at 80A RCD in OFF position to the supply cable ground - still just 0.5 Ohms.
From what I can see the insulation fault is in the supply cable to the house or beyond which is why my RCD has not tripped.
Can somebody confirm my theory please?