Getting myself a little confused with this.
Planning on wiring together two 90Ah batteries as per the below;
Where I am getting stuck is battery cable sizing.
The batteries are in effect wired in parallel to balance, this doubles the amps and keeps voltage the same.
So, for the connections between batteries;
- 90Ah batteries
There is the potential for these to balance and therefore max draw is 90A between the batteries
But, for all other wiring, the batteries in parallel double the amps, so I need something that will handle 180A.
As such, my plan is to use 35mm2 wire with a rating of 240A for all wiring.
I will also install a maxi link fuse between the batteries at 125A - Is this the correct place to put the fuse?
Appreciate if someone could double check my thinking!